Sense of ack_write in I2C module seems backwards
I was having issues talking to an I2C device, and I noticed that the sense of the ack_write flag appears to be backwards in the stock I2C interface module.
From the i2c_controller.luc:
// Write interface
input data_in[8],    // data to write
input write,        // start write signal (1 = start write)
output ack_write,    // was the last write acknowledged (1 = ack, 0 = no_ack)
This seems reasonable, however lower down we see:
        // Write a byte
        States.WRITE:
            // if we aren't on the acknowledge bit
            if (bit_ctr.q != 8)
                sda_value = data.q[7]     // write the MSB of data
            // otherwise, if the clock counter is 0
            else if (scl_reg.q == 0)
                ack_write_reg.d = sda // read the acknowledge bit
To acknowledge a message, an I2C peripheral would pull the sda pin low, and so a value of 0 would be written to ack_write. It seems like this should be:
                ack_write_reg.d = ~sda // read the acknowledge bit
And we can see that the correct negation is performed for the ack_read bit:
        // Read in a byte
        States.READ:
            // if we at the end of the 8th bit or later
            if (bit_ctr.q == 9 || (bit_ctr.q > 7 && scl_reg.q >= c{2b11, ($width(scl_reg.q)-2)x{1b0}})) {
                sda_value = ~ack_read_reg.q // write the acknowledge bit
Am I missing something?
Excellent catch. I’m not sure how that managed to be wrong for so long but I just confirmed it was wrong in Alchitry Labs V1 too.
I just fixed it so in the next release it’ll be changed.